Bob could you elaborate on the difference?????
But on the OP I have used pretty much one brand of these for the last decade.
4120B But assume problems can be simular on other makes. A dead battery can make one chirp - but sometimes that chirp can set off the all of them. But the same can happen if one is not powered by AC.
Recently I learned while having 1/2 a remodel occupied, the other under construction - That if the interconnect wire is accidently grounded a simular condition will occure.
Other
mystery situations that got solved:
- Dusty house
- Return or incomming HVAC wafting dust around.
- Dust damaged detectors - not having detectors covered during any phase of construction can fill the little chamber with dust that will get moved in any current of air. Blow in the chamber, if it goes off replace it - you will not be able to get it out...
- SCENTED CANDLES
- Air freshener - this one nearly killed me! It was in a commercial building with a supervised system that I pulled and terminated for a 'parts and smarts' shop. A timed air freshener in a bath room would periodically go off right next to a return air and set off the smoke in the duct work - All hell would break loose - it took a week to figure out.
- Humidifiers
- Defective detector...