I kind of feel like an idiot, but I have a lot of divergent projects going on, and this one is giving me a headache.
If anyone would like to shed some light, I would be grateful.
I have a site with no grid power.
There is a 45kVa generator. 26kW at single phase.
I wired it for single phase, now he wants it changed over to 3 phase.
There is a 90 Amp main breaker on the generator.
26kW at 240 Volts is 108 Amps.
45kW at 208 Volts is 125 Amps (roughly).
First, why the 90 Amp breaker?
2, do I size the feeder for 125 Amps, or 90 Amps?
Can I size it as a 90 Amp service, because the "service disconnect" is on the generator?
I'll need to size the conductors for 125%, as it will have continuous loads.
If anyone would like to shed some light, I would be grateful.