Skelufteay
 - Denver, Colorado
I was asked for some advice on a potentially burned breaker, and am kind of stumped on what to do next.  I have some experience in electrical troubleshooting with Solar, but building wiring is still a little new to me.  So any advice you can give would be awesome (and I know enough not to shock myself or damage things).
History on building:
It is a warehouse (1.2k sqft) built in the 70's, originally used for storage, then modified to be a call center, and now it is a theatre with office. Due to all these changes, outlets have been added, exit signs have been added, and the circuit breaker is more or less unmarked and illogical (figuring out marking will be my next project).
A few months back, the office circuit was overloaded and the breaker tripped (a space heater was turned on the same time as the microwave or something like that). When we turned the breaker off, then on again, half of the outlets came back on, but one outlet and the exit signs did not (yes, I know they should be on a dedicated circuit but for whatever reason they are not). This strikes me as very odd, since (I believe) each breaker should only have one wire and all the devices are connected in series. From what I am gathering, I think there are two lines on the same breaker, as some outlets work but others do not.
What I have tried so far:
I tested the outlet that was not working (its a 4 plug box, made of two receptacles with 2 sets of 3 prongs each), for continuity (while breaker off).
My plans for continued troubleshoot:
Not sure what else to add, so if there is more information needed please let me know and I can find it out. Thank you for helping me with this!
- The negative wire is continuous with the negative side of the outlet
 - The positive wire is continuous with the positive side of the outlet
 - The neg/pos/GND wires are continuous with the wires from one receptacle to the other (so i know that the lines between them are alright)
 - The negative to positive side of the receptacle do not have continuity (it beeps once then goes silent) ... to me this means the outlet has a short and needs to be replaced, as I checked other outlets in the same manner and they had continuity from neg to pos when metering the left/right holes.
- After replacing both outlets in this box, the signs did not come back on, and the outlet is not working still. But the other outlets on the circuit are working.
 - (I am thinking someone in the building's history took the dedicated line of the exit signs and spliced in an outlet for the office, as it is one of the lines that runs from ceiling to ground on the exterior of the wall).
- I did not see a GFI in the breaker panel, but will re-look and see.
 - test continuity of the lines from breaker to outlet to test lines to see if they are still good (is it best to take the GND and pos wire (then GND and Neg) and disconnect from outlet and breaker, join them on the outlet side and meter on the breaker side?)
 - Test for ground fault: Disconnect the circuit from its power source ? remove the terminals at the panel ? and disconnect the load (device, or devices if they?re lights) from the circuit. Turn all switches for that circuit to the ?on? position. Place the leads of the multimeter, set to the ohmmeter function, across the positive and negative sides of the circuit. A reading of infinite ohms means the circuit is good and the device is bad; a reading of less than infinity means there is a problem in the wiring.
 - Check the signs for blown fuses ... though they did run on backup battery while the power was out, but now those batteries are dead and the theatre needs them light for fire code, as you know. I guess the fuses could be on the incoming line of power, but allow for battery to operate when they blow.