Customer complaint is that after apporx. 30 minutes of running the spa in the heat mode, the GFCI breaker in the panel will trip. He can reset and run for another 30 minutes, and it will trip again.
Need troubleshooting tips.
Installation is as follows:
Install 50 amp 2-pole GFCI breaker in main panel; install (3) #6 and (1) #10 THHN copper conductors from panel in approx. 8' of 3/4" flex to a deep junction box in attic. Bond junction box with #10 to grounds. Run apprx. 50' of 6/3 Romex across attic to another junction box, and bond. Run approx. 5' of 3/4" flex and 8' of 3/4" EMT, with (3) #6 and (1) #10 THNN copper conductors, along exterior wall, to a 50 amp 4-prong receptacle. Attach 90 degree cord cap to approx. 10' of 6/4 SO cord and connect to spa control panel.
Need to know if there is an area in the installation that may be causing this problem.
Thanks for your help.
Sean
Need troubleshooting tips.
Installation is as follows:
Install 50 amp 2-pole GFCI breaker in main panel; install (3) #6 and (1) #10 THHN copper conductors from panel in approx. 8' of 3/4" flex to a deep junction box in attic. Bond junction box with #10 to grounds. Run apprx. 50' of 6/3 Romex across attic to another junction box, and bond. Run approx. 5' of 3/4" flex and 8' of 3/4" EMT, with (3) #6 and (1) #10 THNN copper conductors, along exterior wall, to a 50 amp 4-prong receptacle. Attach 90 degree cord cap to approx. 10' of 6/4 SO cord and connect to spa control panel.