Troubleshooting a 277 emergency light

Status
Not open for further replies.

naplespete57

Member
Location
Eastern Kentucky
Occupation
Project Manager in Conveyor Industry
277 volt emergency light is not working at a plant I am working at. So far I have replaced the battery, didn't help. I do have 277 coming in and when I press the test button the lights come on ever so dimmly for a a second or to. Have inspected for loose wires or burn spots but have found neither. Is there anything else I can do besides replacing the unit?

Thanks as always!
Pete
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
277 volt emergency light is not working at a plant I am working at. So far I have replaced the battery, didn't help. I do have 277 coming in and when I press the test button the lights come on ever so dimmly for a a second or to. Have inspected for loose wires or burn spots but have found neither. Is there anything else I can do besides replacing the unit?

Thanks as always!
Pete

Sounds like the charger board has gone out.
I'd go to the supply house and buy another light and be done with it.
 

satcom

Senior Member
277 volt emergency light is not working at a plant I am working at. So far I have replaced the battery, didn't help. I do have 277 coming in and when I press the test button the lights come on ever so dimmly for a a second or to. Have inspected for loose wires or burn spots but have found neither. Is there anything else I can do besides replacing the unit?

Thanks as always!
Pete

Usually it is always more cost effective, to just replace the unit.
 

JES2727

Senior Member
Location
NJ
I've had similar problems with the same type of fixture. I don't waste time with them anymore. When they fail I either replace the fixture or remove the battery altogether and install an LZ-2 nearby.
 