I'm troubleshooting a paint booth and have come to this point...I think the Honeywell Ignition Transformer (Q652B1006) might be defective because the system faults out when the pilot light should be lit. How do I test the secondary (14kv) of this transformer if my meter is only rated at 1000v?
Lots of possibilities and troubleshooting will be based on knowing what should be happening at each point of the process.
A: One possible scenario:
1. Pilot gas valve turns on.
2. Spark fires and stays on for awhile.
Meanwhile a thermocouple in the pilot flame is heating up and
3. Energizes a circuit that allows the pilot gas valve to stay open after the controller turns off the spark. Main burner is turned on as needed.
4. Otherwise a fault is noted and the equipment shuts down.
B: more likely scenario with modern equipment:
1. Pilot gas valve turns on.
2. Spark fires intermittently, and between spark pulses electronics in the controller check the conductivity between the electrodes to see whether ionization (indicating flame) is present.
3a. If the flame detector fires within a programmed timeout, the spark is shut down and the flame stays lit. Main burner turns on as needed.
3b. If the flame detector ever shows the flame going out, or it is never lit, the system faults and shuts down.
Yet another:
C: Like scenario B but with the spark igniter directly lighting the main flame, so that as the main flame cycles on and off there is no constantly or intermittently lit pilot.
Common to all of them is that shortly after the spark is seen, something should light. If you see (or hear) a spark but no flame results, it is most likely that there is a problem with the gas valve, not the igniter.
On the other hand, if you see a spark, then a flame, but the system then shuts down, either the thermocouple or the flame sensor (usually incorporated into a spark generator module which is more than just a transformer) is faulty.
If you hear a spark but do not see it at the pilot ignitor, possibly there is a short in the ignitor wiring and the spark you hear is in the wrong place.
If there is a problem with the gas valve itself, you are no longer just acting as an electrician and will have to choose how far you want to continue in troubleshooting and repair.