One of our facilities had several fuses fail on the Control Power Transformer in the High Voltage Line-up last week. (A&C Phase)
13.8KVBUS--------->FUSE DRAWER------>CPT XFMR------->120/208PanelBoard
We tested the transformer for a fault, and it tested out good.
We checked the panelboard that it feeds for a fault, and it tested out good.
We isolated the load from the Control Power Transformer by shuting off the main in the panelboard.
We reloaded the fuses into the CPT fuse drawer/rack and rolled the drawer/rack back in.
Both A&C fuses failed again. (No load on the CPT transformer)
We called in a contractor to test everything on the system.
They tested everything and could not find a fault on the system.
TTR, Power Factor, Megger tested the transformer. (Good)
Megger tested the line & load cables (Good)
Megger tested the 120/208V panelboard. (Good)
Megger tested the CPT Fuse rack holders/insulators. (Good)
Looked into the shutter windows that the fuse rack mates into (bus stabs looked good)
We verified that we have 3-phases of 13.8KV power on the main primary bus. We re-loaded the fuse into the CPT fuse drawer/rack and rolled the drawer/rack back in.
Both A&C fuses failed again.
We all spent time scratching our tails on this one.
What would you look at next?
Any time is greatly appreciated.
13.8KVBUS--------->FUSE DRAWER------>CPT XFMR------->120/208PanelBoard
We tested the transformer for a fault, and it tested out good.
We checked the panelboard that it feeds for a fault, and it tested out good.
We isolated the load from the Control Power Transformer by shuting off the main in the panelboard.
We reloaded the fuses into the CPT fuse drawer/rack and rolled the drawer/rack back in.
Both A&C fuses failed again. (No load on the CPT transformer)
We called in a contractor to test everything on the system.
They tested everything and could not find a fault on the system.
TTR, Power Factor, Megger tested the transformer. (Good)
Megger tested the line & load cables (Good)
Megger tested the 120/208V panelboard. (Good)
Megger tested the CPT Fuse rack holders/insulators. (Good)
Looked into the shutter windows that the fuse rack mates into (bus stabs looked good)
We verified that we have 3-phases of 13.8KV power on the main primary bus. We re-loaded the fuse into the CPT fuse drawer/rack and rolled the drawer/rack back in.
Both A&C fuses failed again.
We all spent time scratching our tails on this one.
What would you look at next?
Any time is greatly appreciated.