cohosilver
Member
Situation: Square D 100A 277/480V I-line circuit breaker that feeds a Sqaure D 277/480V NF MLO panelboard is tripping for no obvious reason. There is no load on the panelboard (A-13.3A, B-23.6A, C-0.7A). There is no load on the branch circuits at the panelboard which only has 6 20A circuit breakers. There is no physical damage to the feeders or branch circuit conductors and the feeders were just replaced because the circuit breaker had tripped so it is unlikely that it is the conductors. The feeders are a #2 awg 4/C CT Cable Tray Cable. The breaker has tripped 4 times and the 4th time it tripped the 400A Main Breaker for the I-line panel. (Note - I am not the guy repeatedly resetting the breaker, it is the customer). The breaker does not immediately trip, it can hold for hours so everything is working whenever I arrive.
I am going to replace the 100A circuit breaker at the I-line panel with the hypothesis that it is a bad 100A circuit breaker. Other than meggering the cables to test the insulation resistance (I do not have a megger available) is there any sugggestions of what the issue could be?
I am stumped.