Scenario:
did a service call for tripping AFCI breaker at an apartment complex where the company i work for had done some remodel work adding receptacle outlets. Traced the problem to a severely nicked (sloppy work by installer) neutral wire at the termination screw of a receptacle. This receptacle was on a 'dead end' of the circuit, eg. no subsequent devices attached.
The problem:
The resident called the complex office to report the lack of lights in her apartment and the complex maintenance guy came to investigate. According to the resident and the maitenance guy, when he reset the breaker, a receptacle that had a TV/DVD player plugged into it 'shot sparks' as the breaker re-tripped. The TV/DVD were NOT plugged into the receptacle with the bad neutral wire. After i completed the repair on the receptacle with the bad neutral wire and reset the breaker, the TV/DVD did not work. I tested the receptacle, and pulled it out to examine it, and found no problems.
The Question:
I'm sure the complex will send a bill for the fried TV/DVD to the company. Could the nicked neutral on a 'dead end' receptacle have caused the 'flash' at the receptacle the TV was plugged into? If not, what else could have caused the 'flash'? The AFCI breaker worked fine after the repair on the nicked neutral wire.
Any ideas/input much appreciated
did a service call for tripping AFCI breaker at an apartment complex where the company i work for had done some remodel work adding receptacle outlets. Traced the problem to a severely nicked (sloppy work by installer) neutral wire at the termination screw of a receptacle. This receptacle was on a 'dead end' of the circuit, eg. no subsequent devices attached.
The problem:
The resident called the complex office to report the lack of lights in her apartment and the complex maintenance guy came to investigate. According to the resident and the maitenance guy, when he reset the breaker, a receptacle that had a TV/DVD player plugged into it 'shot sparks' as the breaker re-tripped. The TV/DVD were NOT plugged into the receptacle with the bad neutral wire. After i completed the repair on the receptacle with the bad neutral wire and reset the breaker, the TV/DVD did not work. I tested the receptacle, and pulled it out to examine it, and found no problems.
The Question:
I'm sure the complex will send a bill for the fried TV/DVD to the company. Could the nicked neutral on a 'dead end' receptacle have caused the 'flash' at the receptacle the TV was plugged into? If not, what else could have caused the 'flash'? The AFCI breaker worked fine after the repair on the nicked neutral wire.
Any ideas/input much appreciated