troubleshooting...

Status
Not open for further replies.

journeyman0217

Senior Member
Location
philadelphia,pa
ran into this problem today was wondering if anyone could lend some advice...There are 16 pendant lights in a local shop, all 16 light up when switch is thrown but the last 6 were noticeably dimmer than the others. I read 125 volts at fixture 1, 124 volts at fixture number 10 and read 25 volts on 11,12,13,14,15 and 16 ( the fixtures that were dim). any ideas?
 
High resistance connection somewhere between no 10 and 11. Or grounded conductor is open somewhere after no 10 but does have a high resistance fault to ground.
 
I was thinking maybe mc connector can be tighten to much possibly causing high resistance connection....?

Not unless it has severed the mc jacket and has made contact with neutral conductor.
But I would be looking at wirenut connections first.....especially jam packed junction boxes.
 
Not unless it has severed the mc jacket and has made contact with neutral conductor.
But I would be looking at wirenut connections first.....especially jam packed junction boxes.
Would have to sever the neutral conductor as well, pinching into the ungrounded conductor would result in high current and tripping overcurrent device unless there is poor grounding/bonding, but then shock hazards would increase.
 
High resistance connection somewhere between no 10 and 11. Or grounded conductor is open somewhere after no 10 but does have a high resistance fault to ground.

I agree -- the poor connection is at #10 or #11. Your voltage readings don't tell us what you are measuring to. . . is it the neutral conductor (white) or is it the EGC - equipment grounding conductor (the MC sheath / green)?

Assuming the voltage measurement is between energized conductor and EGC, remake the energized splices in #10 and #11.
 
High resistance connection equal heat! Consider the voltage droop and the resulting heating watts. It is best to locate and resolve the problem. P(in watts)=I x V. If you have a 90v loltage drop and a given current supplying those dimmed lights the result is the heating watts a the defective connection which is a serious issue.
 
High resistance connection equal heat! Consider the voltage droop and the resulting heating watts. It is best to locate and resolve the problem. P(in watts)=I x V. If you have a 90v loltage drop and a given current supplying those dimmed lights the result is the heating watts a the defective connection which is a serious issue.
Yep. that failing connection probably won't be too hard to find, look for the toasted insulation on the conductors near the connection.
 