Hello everyone, I don't post much, but I do come to the forum often and you guys are a valuable source of knowledge and experience for me! I know this is the place to ask a question when I can't get an answer anywhere else.
My basic question is this - When measuring voltage drop across a device such as a breaker, or fuse, or switch to check for loose/faulty components or terminations, what is an acceptable range? I usually work with 120-240VAC. I know 0.0V is ideal, and may be expected for a new install, but I'm concerned with devices that have been in use for some time.
Checking VD is part of my troubleshooting process for breakers and such. But I'm not sure where to draw the line between pass and fail for that test. In the past, I've replaced a main breaker that had a 5V drop between the line side lug and the load side busbar, and once I removed it, it was obvious that it was damaged. So I know that large of a VD is unacceptable. But my service call today was checking a fuse in an old fuse box, and I only measured 0.4V from the main line side lug to the load side screw on the fuseholder. But when there was a load on that circuit, the fuse was hot to the touch. I measured VD across the other fuses in that box, and they ranged from 0.1 to 0.3V, and none felt as hot as the first fuse did. I imagine that every situation will have different allowances, but I would appreciate feedback on what to be concerned about.
My basic question is this - When measuring voltage drop across a device such as a breaker, or fuse, or switch to check for loose/faulty components or terminations, what is an acceptable range? I usually work with 120-240VAC. I know 0.0V is ideal, and may be expected for a new install, but I'm concerned with devices that have been in use for some time.
Checking VD is part of my troubleshooting process for breakers and such. But I'm not sure where to draw the line between pass and fail for that test. In the past, I've replaced a main breaker that had a 5V drop between the line side lug and the load side busbar, and once I removed it, it was obvious that it was damaged. So I know that large of a VD is unacceptable. But my service call today was checking a fuse in an old fuse box, and I only measured 0.4V from the main line side lug to the load side screw on the fuseholder. But when there was a load on that circuit, the fuse was hot to the touch. I measured VD across the other fuses in that box, and they ranged from 0.1 to 0.3V, and none felt as hot as the first fuse did. I imagine that every situation will have different allowances, but I would appreciate feedback on what to be concerned about.