Even with that wouldn't the L-L voltage still be 480V?Bad neutral to ground bond.
I think single phase is set up line to ground, ie 0-480 not 240-0-240 and not single phase from a wye system where you have 277 to groundEven with that wouldn't the L-L voltage still be 480V?
I would guess a bad/lost phase and something is backfeeding to get a reading on the lost phase/leg.
All I've heare is that it is used for highway lightingI've never heard of a 480V single phase service being used. Is this a PoCo supplied voltage or is this in house supplied (in other words, your transformers not PoCo's)?
Single phase system 480v to ground.....1 leg has 480v to ground and the other has 235v to ground...the 2 together is 280v...any suggestions on what is causing this
OP needs to clarify and be more specific. I am not exactly sure where and how is measurements are being taken and they make no sense.
Still don't think he should ever see 480 to ground, but that depends on exactly what his source is. I'm presuming 240 - 0 - 240. We have many those around here for irrigation systems where three phase primary lines isn't available and customer uses a phase converter to get three phase.Even with that wouldn't the L-L voltage still be 480V?
I would guess a bad/lost phase and something is backfeeding to get a reading on the lost phase/leg.
I'm guessing most places it has 240 volt center tap and that is what is grounded. It certainly would be more common here vs 480 volt two wire system.480 single phase IS common for highway lighting and as already stated, the OP should tell us about the application and the service configuration.
Why?We need more info. Possibly the POCO has a blown fuse on their transformer bank causing fluctuating voltage dependent on load. 480 volt single phase is weird.