Dale lee

Member
Location
Fort myers Fl
Occupation
EC
Today I was working on a remodel, working on a 4G switch while low volt guys were working on a lutron system. In trying to troubleshoot tripping circuits I had all my neutrals disconnected. Found the one making the circuit trip, and as I’m testing I find 120v neutral to ground on every single neutral in the box. My mind is boggled as some of these are switch legs coming straight out of fixtures. I think maybe backfeeding but if that were the case what about every other neutral not interconnected. I checked the main panel for a possible back feed to neutral bar to explain the other neutrals but it all checks out. So I tie them all together and it does not trip but now I have 1v and all is working fine. Can someone explain this to me?
 
I’m assuming something to do with how the house was wired previously, works fine just was concerned of causing damage in the future if left unattended and I don’t have time to trace out someone else’s nonsense.
 
So if u unhook the noodle that previously made the ckt trip and now it’s not and your getting 120v on it sounds like the ckts not tripping because it doesn’t have a ground reference and you probably have a staple or nail touching the hot to the noodle. Or if there are
Power packs maybe one of them is shorted
 
Answers would depend on the age of the house. Under which NEC it was wired
White does not equal neutral. We were not always required to ID a switch leg.
Neutrals were not always required at switches.
Open circuit voltage of Neutral to EG would be 120 volt.
Measuring 1 volt between a loaded neutral conductor and EG would be VD.
 