TWGJ24

Member
I have a 12"x12"x10' Trough under 4 panels with (2) 2" EMT Conduits that are less than 24"s in length to each. I have 120 current carrying conductors in this trough splice free going to the designated panels non lighting circuits. All are number 12. Using article 300 and 310. I want to be sure I am correct in using these on a 20A Breaker since I have already derated the number 12 once from 30A to 24A at 80 percent. 310.15(b)(2)(a) i know is used as necessary for ambient temp. Please someone explain.
 
You need to look at 376.22 (A) and (B)

376.22 Number of Conductors and Ampacity
The number of conductors and their ampacity shall comply with 376.22(A) and (B).

(A) Cross-Sectional Areas of Wireway. The sum of the cross-sectional areas of all contained conductors at any cross-section of a wireway shall not exceed 20 percent of the interior cross-sectional area of the wireway.

(B) Adjustment Factors. The adjustment factors in 310.15(B)(3)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions of 310.15(B)(5), exceeds 30. Conductors for signaling circuits or controller conductors between a motor and its starter and used only for starting duty shall not be considered as current carrying conductors.
 