Re: Trough Fill
-Frank,
What I can interpret in your post:
310.15(b)(2)
-The "18 nipples,not being your problem-.
The problem as I interpret being:
366.22(a)- is exceeding 30 current carrying conductors-.The 20% fill may or may-not be a factor,given the fact of you have not denoted in your post,in the knowing exactly what all is in the trough..
epending on the way your conductors,are laid out entering this enclosure above the three (3) panels,can you install dividers (end caps internal inside enclosure), to section-out the areas of this trough above the panels.In reducing the #'bers of conductors as a whole, to the given (sectioned) areas.Provided,your not exceeding the 20% fill and 30 currect carrying conductor limitation, of the sectioned areas?
In reading your post,I suspect this installation,in fact already exsist.And not knowing how many current-carrying conductors,are passing through this enclosure,to the denoted (3)200 ampere panels..(have you got more than thirty current carrying conductors,to EACH panel)
Noted: I'm sure in my response to this thread,will raise up some comments..Trying to think off-the-fly...More than likely, non- workable solution in this situation...