L Lefty0824 Member Location New Jersey Mar 24, 2011 #1 I'm doing a multifamily dwelling service with a trough what are the bonding requirements to bond the trough?
I'm doing a multifamily dwelling service with a trough what are the bonding requirements to bond the trough?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 24, 2011 #2 If it's the trough containing service conductors, 250.92(A) requires it to be bonded. 250.92(B) gives the acceptable method of bonding.
If it's the trough containing service conductors, 250.92(A) requires it to be bonded. 250.92(B) gives the acceptable method of bonding.
mark32 Senior Member Location Currently in NJ Mar 24, 2011 #4 Hey Lefty, check out the thread I started a short while ago http://forums.mikeholt.com/showthread.php/134396-POCO-diagram-bonding-question Larry and Augie contributed an idea or two.
Hey Lefty, check out the thread I started a short while ago http://forums.mikeholt.com/showthread.php/134396-POCO-diagram-bonding-question Larry and Augie contributed an idea or two.