I noticed thag after posting, and wondered what was going on. The panel is protected at 200 amps and wire is sized for 200 amps but without 200 amp fuses in the 400 amp disconnect it of course violates tap rules.What size fuses are in the 400 amp disconnect switch? #3/0 is only good for 200 amps.