Situation:
Power Company CT cabinet. I must exit the top of the CT cabinet with the customer side service conductors. My preference is to use a 4” nipple to go up into this trough. The trough will extend past the side of the CT cabinet so that I can drop down in 4” conduit to a trough that will be below my disconnects. (Before you ask, and it has no bearing on the question I’m about to ask anyway, because of a design problem I can not extend the top trough over and feed my disconnects from the top.)
Does 314.28 apply to sizing the trough? Or am I missing something. If I must use 314.28 then I will have a gigantic junction box that looks like crap.
4” x 6 times the trade size = 24” plus 4” for the other opening in the same wall.
I swear I have put a ton of troughs up in my career and I’ve never put one up this large in this deminision. Have I always done it wrong but never been caught, or am I having a senior moment?
Power Company CT cabinet. I must exit the top of the CT cabinet with the customer side service conductors. My preference is to use a 4” nipple to go up into this trough. The trough will extend past the side of the CT cabinet so that I can drop down in 4” conduit to a trough that will be below my disconnects. (Before you ask, and it has no bearing on the question I’m about to ask anyway, because of a design problem I can not extend the top trough over and feed my disconnects from the top.)
Does 314.28 apply to sizing the trough? Or am I missing something. If I must use 314.28 then I will have a gigantic junction box that looks like crap.
4” x 6 times the trade size = 24” plus 4” for the other opening in the same wall.
I swear I have put a ton of troughs up in my career and I’ve never put one up this large in this deminision. Have I always done it wrong but never been caught, or am I having a senior moment?