I went through a thread from years ago, and I had this follow up question:
A 240 volt, 4500 watt hot heater heater connected to a 208 volt panel will operate at 75% of its nameplate wattage. so 4500 watts x .75 = 3375 watts.
When performing feeder / service calculations from article 220, whether standard or optional it is stated you have to use nameplate ratings. So we 4500 watts. Is this correct?
And when do you use the 3375 watts? Is it when you calculate the branch circuit ratings?... the breaker and wire size?
Thanks.