This is an excerpt from a government document explaining the requirements for facility power for isolation transformers. It is old and note the reference to NEC 250-5 which doesn't seem to have a direct map to the more recent NEC numbering style. I think it is referring to some section on separately derived systems.
Here's the quote: "It should be installed per NEC 250-5(d) as a separately derived system and, as such, establishes a new fault protection subsystem. It should not be tied to the green wire serving the power main side, as this defeats the intent of both the NEC for protection and the use of this type of transformer to breaker ground loops. Further, some isolation transformers can be designed with the ground and neutral conductors being common to the primary and secondary windings. This reduces the siolation effectiveness of the transformer."
So I understand wanting a transformer secondary whose neutral is not common to the input neutral (if it even has an input neutral). However, is there any legal way to not ground the secondary, or ground it in such a way that it doesn't work back to the primary side "green wire"? I don't see how when this is installed in an industrial building with building steel being used as the grounding path (this is the electrode present throughout the building and I would expect it to be electrically continuous).
Here's the quote: "It should be installed per NEC 250-5(d) as a separately derived system and, as such, establishes a new fault protection subsystem. It should not be tied to the green wire serving the power main side, as this defeats the intent of both the NEC for protection and the use of this type of transformer to breaker ground loops. Further, some isolation transformers can be designed with the ground and neutral conductors being common to the primary and secondary windings. This reduces the siolation effectiveness of the transformer."
So I understand wanting a transformer secondary whose neutral is not common to the input neutral (if it even has an input neutral). However, is there any legal way to not ground the secondary, or ground it in such a way that it doesn't work back to the primary side "green wire"? I don't see how when this is installed in an industrial building with building steel being used as the grounding path (this is the electrode present throughout the building and I would expect it to be electrically continuous).