Hi,
I'm a technician for an air compressor company. A customer had me look at a 55KW VFD compressor that has been faulting out. Fault code corresponds to missing phase.
He swears they have good power. Fuses tested good at disconnect.
The following readings are taken with our load completely disconnected from incoming power and readings were taken ABOVE Z the fuses so it's just their BUS power to their disconnect l.
My Fluke reads the following:
L1-L2=337v
L2-L3=337v
L3-L1=470v
L1-G=467v
L2-G=110v
L3-G=470v
The customer had a Klein DMM not listed as RMS
His meter saw:
L1-L2=0v
L2-L3=0v
L3-L1=470v
He then got his equipment guy over with his KLEIN DMM and repeated the same results as his KLEIN got.
I think it is grounded B phase and I think there's a problem with their BUS/BUS fuses
He claimed my Fluke was broken so I got my other fluke 87 a Greenlee RMS and a Menard's RMS meter and all of them repeated my weird readings.
Please help me understand what's going on with their power and why do or meters read so differently?
Thanks
Jordan
I'm a technician for an air compressor company. A customer had me look at a 55KW VFD compressor that has been faulting out. Fault code corresponds to missing phase.
He swears they have good power. Fuses tested good at disconnect.
The following readings are taken with our load completely disconnected from incoming power and readings were taken ABOVE Z the fuses so it's just their BUS power to their disconnect l.
My Fluke reads the following:
L1-L2=337v
L2-L3=337v
L3-L1=470v
L1-G=467v
L2-G=110v
L3-G=470v
The customer had a Klein DMM not listed as RMS
His meter saw:
L1-L2=0v
L2-L3=0v
L3-L1=470v
He then got his equipment guy over with his KLEIN DMM and repeated the same results as his KLEIN got.
I think it is grounded B phase and I think there's a problem with their BUS/BUS fuses
He claimed my Fluke was broken so I got my other fluke 87 a Greenlee RMS and a Menard's RMS meter and all of them repeated my weird readings.
Please help me understand what's going on with their power and why do or meters read so differently?
Thanks
Jordan