tv outlet 5.5 ft above electric baseboard?

Status
Not open for further replies.

whofrankw

Member
Location
milford nj
I've been searching and I know I can't put outlets above electric heat but can I put a TV outlet 5.5 ft above electric heat. Seems reasonable since no cords will be dropping over the heater
 
Anything about receptacles over electric baseboard heaters is going to be in the paperwork that comes with the heater, there's nothing in the nec.

Unless you count

II. Installation
424.9 General.

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.
 
Unless you count

II. Installation
424.9 General.

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.

I believe Dave's point is that there is no specific code section prohibition nor allowance in regards to installing receptacles above baseboard heat.

The informational note merely reminds one of following 110.3(B) IMO. Informational notes are note actually code per se.

90.5(C) Explanatory Material.
Explanatory material, such as references to other standards, references
to related sections of this Code, or information related to a Code rule,
is included in this Code in the form of informational notes.
Such notes are informational only and are not enforceable as requirements of this Code.
 
Unless you count

II. Installation
424.9 General.

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.

I am sure Dave knew about that just like I am fairly certain you know that is not a code section.
 
I am sure Dave knew about that just like I am fairly certain you know that is not a code section.

But he said "there's nothing in the nec." That is not correct. He did not say "that there is no specific code section prohibition nor allowance in regards to installing receptacles above baseboard heat"
 
But he said "there's nothing in the nec." That is not correct. He did not say "that there is no specific code section prohibition nor allowance in regards to installing receptacles above baseboard heat"
And I'll say it again. There's nothing in the NEC that says you can't put a receptacle above an electric baseboard heater.
 
But he said "there's nothing in the nec." That is not correct. He did not say "that there is no specific code section prohibition nor allowance in regards to installing receptacles above baseboard heat"

I find this to be very high on the nitpicky scale.

Next time it comes up I will likely say it just like Dave.:D
 
So, if Dave said that there "was nothing in the NEC about branch circuit voltage drop"?
 