Google gave my this
http://www.currenttechnology.com/
And this
http://www.neccode.com/mojonewsarchive/LSP-HTML/HTML/TVSS-Protection-Questions-and-Answers~20040708.php
And of course a bunch of poeple that want to sell me one.
My questions have to do with this design that has TVSS on the emergency side of the transfer switches. Genny feed comes into a gutter that feeds 2 transfer switches. This is where the TVSS will be installed. No TVSS on normal power side.
1) This is not a SDS. Wouldn't a surge cause potentially dangerous currents on POCO's grounded conductor?
2) Why would a gen-set require a TVSS if it has a voltage regulator.