I've searched the forum but couldn't find the answer, probably because it's so obvious that I just can't see it.
Im looking at a large (4000 A MCB main panel) commercial installation and a bunch of smaller distribution panels. Each distribution panel (other than the Main) has a TVSS mounted very close to the panel through a 60A breaker with AWG #10.
Now, here's my problem. I know that under normal conditions the TVSS draws no current so AWG #10 is obviously OK. However, the ampacity of #10 THWN is only 35A. So, in the case of a partial failure of the TVSS the current could be greater than 35A and less than 60A. That, to me, feels wrong because it is in excess of the conductor's ampacity, could continue indefinitely, and thus create a real problem. I am aware that with a complete TVSS failure the breaker would interrupt very quickly what is probably a massive overcurrent.
NEC Section 285 doesn't address this and the only basis I would have for my argument is section 240 but I'm not totally comfortable with it.
Should I worry about that partial failure and require that the CB be suitable for the conductor size? Or, if the TVSS manufacturer specifies a particular OCPD that an appropriately sized conductor be used?
Heinz R.
Im looking at a large (4000 A MCB main panel) commercial installation and a bunch of smaller distribution panels. Each distribution panel (other than the Main) has a TVSS mounted very close to the panel through a 60A breaker with AWG #10.
Now, here's my problem. I know that under normal conditions the TVSS draws no current so AWG #10 is obviously OK. However, the ampacity of #10 THWN is only 35A. So, in the case of a partial failure of the TVSS the current could be greater than 35A and less than 60A. That, to me, feels wrong because it is in excess of the conductor's ampacity, could continue indefinitely, and thus create a real problem. I am aware that with a complete TVSS failure the breaker would interrupt very quickly what is probably a massive overcurrent.
NEC Section 285 doesn't address this and the only basis I would have for my argument is section 240 but I'm not totally comfortable with it.
Should I worry about that partial failure and require that the CB be suitable for the conductor size? Or, if the TVSS manufacturer specifies a particular OCPD that an appropriately sized conductor be used?
Heinz R.