tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Sep 1, 2020 #1 Milbank Mobile Home Pedestal, uses 1" QP breaker. who makes the QP breaker and is there a 30A, 1", pole twin available?
T Todd0x1 Senior Member Location CA Sep 1, 2020 #2 QP is siemens. A 2 pole 30A would be Q230 this would be 2 spaces wide. A 30/30 tandem breaker would be Q3030. Catalog pdf link below, you want page 1-41 https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/2020-04-02/SpeedFax/SF-17-Sect-01-ALL-web.pdf
kwired Electron manager Location NE Nebraska Occupation EC Sep 2, 2020 #3 Check label, that Milbank likely mentions Siemens, GE, Homeline, BR, maybe even other older lines that were absorbed into those I mentioned. Next thing is whether or not it will even accept a twin/tandem breaker regardless of which brand it may be.