Yes, and we generally prefer to call them 'tandem' breakers.Are twin breakers (having two breakers installed where one breaker would normally occupy) in commercial or residential buildings code complaint?
Agreed. You often find both legs of a MWBC put on the same phase.It's the neutrals that are associated with the existing cicuits that are most times not given the attention they deserve when people go moving things around to install them.
Type of occupancy doesn't matter as long as the panel listing is followed. For something like a 40/80 that suremarkp mentioned you could have 40 tandems providing 80 circuits. If the panel were listed as 40/60 then only 20 tandems can be installed.Are twin breakers (having two breakers installed where one breaker would normally occupy) in commercial or residential buildings code complaint?
So true. Ran across this the other day.Agreed. You often find both legs of a MWBC put on the same phase.
I have seen new work with the black and red on the same tandem.
Yes, the AFCIs that do not have a ground fault protection circuit do not have the load neutral connected to the AFCI breaker. The breaker still needs a neutral connection for the electronics that make the AFCI work.Siemens is making tandem arc fault where the neutral does not connect directly through the breaker. In fact, I think their new design even has full 1” type afci nit having the neutral on the breaker. It goes with the rest of the neutrals on the same bar. All these breakers are plug on neutral.
Yes, it seems there's a few guys out there who are completely unclear on the concept and believe that the tandem is supposed to get both wires of the MWBC.So true. Ran across this the other day.
I've seen this called out by home inspectors who were too lazy or didn't know that they need to trace the black and red conductors all the way back to where the cable enters the panel. Seems that the sparky alternated the condcutors when he attached them to the tandem breakers so they were wired correctly. This is all out the window now with the handle tie rules for MWBC's.Yes, it seems there's a few guys out there who are completely unclear on the concept and believe that the tandem is supposed to get both wires of the MWBC.
If GE THQP, were used it been just fine, or a older Challenger, or Crouse-Hinds panel with twins, guess I should include Zinsco/Sylvania, & FPE too.Yeah, I mean I've seen a couple panels where when I looked carefully at everything, every MWBC was doubled up on a single tandem. The probability was near certain it was done on purpose.
If GE THQP, were used it been just fine, or a older Challenger, or Crouse-Hinds panel with twins, guess I should include Zinsco/Sylvania, & FPE too.
If GE THQP, were used it been just fine, or a older Challenger, or Crouse-Hinds panel with twins, guess I should include Zinsco/Sylvania, & FPE too.
If you’re not paying attention to a MWBC, both legs can end up on the same phase using GE THQP.If GE THQP, were used it been just fine, or an older Challenger, or Crouse-Hinds panel with twins, guess I should include Zinsco/Sylvania, & FPE too.
But if using 2 pole ones you shouldn't have any issuesIf you’re not paying attention to a MWBC, both legs can end up on the same phase using GE THQP.