NEC 2017 Section 695.6(C) and section 430.31 both says overload protection for Fire Pump is prohibited.
I have backup generator feeding Fire Pump that has internal overload protection in generator by manufacturer of the generator.
I do see the exception 2 in NEC 2017 section 695.6(C) to overload protection regarding standby generator since I have 124A fire pump load and generator is full load is 601A but that exception is very hard to understand what it means.
Should the generator Not be provided with overload protection or is their anything in NEC 2017 regarding this situation?