This is just for confirmation of what I think I know. Please enlighten me if I'm wrong in my understanding of this topic.
With a multi-wire branch circuit you have to use two separate breakers with a listed handle tie, 210.4(B), 240.15(B)1.
My 2 questions are:
1) Is it allowed to use a 2-pole breaker for a multi-wire Branch circuit (or 3-pole for a 3 phase mwbc)?
2) Outside of this mwbc topic, any branch circuit that has line-to-line loads you have to use a 2-pole breaker with a common trip (two separate breakers with handle tie doesn't qualify)?
I just want some clarification on this issue to make sure I'm not being unjustly critical on fellow workers.
Thanks,
Sky
With a multi-wire branch circuit you have to use two separate breakers with a listed handle tie, 210.4(B), 240.15(B)1.
My 2 questions are:
1) Is it allowed to use a 2-pole breaker for a multi-wire Branch circuit (or 3-pole for a 3 phase mwbc)?
2) Outside of this mwbc topic, any branch circuit that has line-to-line loads you have to use a 2-pole breaker with a common trip (two separate breakers with handle tie doesn't qualify)?
I just want some clarification on this issue to make sure I'm not being unjustly critical on fellow workers.
Thanks,
Sky