As you can see from the image, I am attempting to power two new chillers from a single feeder. The service switchboard MCB is 3000Amps at 480Volts, 3-phase. I want to feed the chillers from one circuit breaker for two reasons: 1. The distance between the 1600A circuit breaker and the chillers is considerable, and I would only like to run 1200Amps of copper instead of 1200Amps two times, and 2. I do not think I can fit more than a single new 1600A circuit breaker into the existing 3000A service switchboard.
The chillers will not run at the same time. BMS programming will ensure this.
I have a couple of questions:
1.) This design looks strange, so I am wondering if anyone has done something like this before and has run into any issues, especially code-related issues?
2.) Each chiller's cutsheet says that the chiller requires a 1600A max OCPD and 1200A MCA. Would the local disconnect switches need to be 1600A or 1200A?