Due to last minute design changes, wondering if a 6AWG wire can be tapped with a 4/0 wire on the load side of CB. It's a control panel, 6 AWG wire tap is allowed. It's a one conductor lug terminal.
Quick answer is NO, 110.14(A) violation. But maybe there are any considerations allowing a comparatively small wire to be connected together with a much larger wire. Other solutions is to use multiwire terminals, but it's not desirable in this situation.