two conventional water heaters on a subpanel
RustyShackleford
NC
electrical engineer
I have a subpanel with two branch circuits, driving two water heaters, rated at 3500 and 4500 watts, respectively. What ampacity is required for the feeder to the sub panel ? Is it necessary to apply the 25% continuous-load margin to both loads, or just the largest load ? If the former, then 125% * (4500+3500) / 240 or about 42 amps, if the latter then (4500*125% + 3500)/240 = 38 amps.
I believe 422.11(E) gives the requirements for each water heater, but this doesn't seem to apply to the feeder.
I take "conventional" to mean "storage-type," so 422.13 controls. As it specifies a continuous load "for the purposes of sizing branch circuits," it is implicit that for sizing the feeder, you have no continuous loads. Your feeder load is 8000 VA.
Cheers, Wayne
The 125% requirement {422.11(F)in '17} applies to branch circuits. Your feeder can be sized base on the individual wattages. 33 amps
)Typed as wwhitney posted)
So in this particular case it turns out to make no practical difference. You need 8awg wire regardless, and then why would you bother looking for a 35A breaker when you are allowed to use a 40 (or depending on your wiring method, a 50).
Well, if I had to add the 125% up-rated ampacities of the two water heaters I'd need 6awg (if NM-B) and a 45- or 50-amp breaker.
But I don't need to, so thanks for the replies.
Yes, by "conventional" I mean storage-tank style.