RustyShackleford
Senior Member
- Location
- NC
- Occupation
- electrical engineer
I have a subpanel with two branch circuits, driving two water heaters, rated at 3500 and 4500 watts, respectively. What ampacity is required for the feeder to the sub panel ? Is it necessary to apply the 25% continuous-load margin to both loads, or just the largest load ? If the former, then 125% * (4500+3500) / 240 or about 42 amps, if the latter then (4500*125% + 3500)/240 = 38 amps.
I believe 422.11(E) gives the requirements for each water heater, but this doesn't seem to apply to the feeder.
I believe 422.11(E) gives the requirements for each water heater, but this doesn't seem to apply to the feeder.