Not exactly the code for what was asked. This one is for different systems such as DC and AC.300.3(C)(1)
C) Conductors of Different Systems.
(1) 1000 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 1000 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway. Secondary wiring to electric-discharge lamps of 1000 volts or less, if insulated for the secondary voltage involved, shall be permitted to occupy the same luminaire, sign, or outline lighting enclosure as the branch-circuit conductors.
Good catch bill , my mind went to that sectionNot exactly the code for what was asked. This one is for different systems such as DC and AC.
I don't have the code handy but if it doesn't specifically say not to, it is allowed. Certainly conductors of the same source but different circuits are allowed, it's done everyday.
I would take it as meaning it also applies to different systems as in SDS's.Not exactly the code for what was asked. This one is for different systems such as DC and AC.
I don't have the code handy but if it doesn't specifically say not to, it is allowed. Certainly conductors of the same source but different circuits are allowed, it's done everyday.
It not for just AC and DC in same raceway, you could have a 480 volt AC and 120 volt AC circuit (they are almost always from separate systems) in the same raceway. Design decisions may commonly lessen how often that may happen.Not exactly the code for what was asked. This one is for different systems such as DC and AC.
I don't have the code handy but if it doesn't specifically say not to, it is allowed. Certainly conductors of the same source but different circuits are allowed, it's done everyday.
If you notice, I said "such as" not "just". That was just one example.It not for just AC and DC in same raceway, you could have a 480 volt AC and 120 volt AC circuit (they are almost always from separate systems) in the same raceway. Design decisions may commonly lessen how often that may happen.