Please see attached sketch shows four tenant spaces separated by demising wall.
I have two incoming electric utility services one 208/120V three phase 800A feeding 6 service disconnects meter stack MLO located in sprinkler room. The second 208/120V 600A feeding service trough with 3 service disconnects located in tenant #1 space
The first electric utility service meter stack six main service disconnects two of them feed tenant #1 space, one of them feed tenant #3 space, other one feed tenant #4 space and sixth one is spare feeding nothing.
The second electric utility service 600A trough service disconnects all three feed tenant #1.
Assume each four tenant spaces are separate buildings. Note sprinkler room is in tenant space #1 enclosed by walls and can only be accessible thru outside door. Not sure if it is even considered part of tenant #1 or not.
Following are the question:
1. Would it be considered code compliant NEC 230.2 a building is only served by one utility service if meter stacks two service disconnect feeding tenant #1 are relocated to be fed from service 600A trough disconnects? That way tenant #1 electric utility would serve only tenant #1 and meter stacks utility would serve multiple tenants but their is no provision that single utility cannot serve multiple buildings. Please let me know your opinions and thoughts
I have two incoming electric utility services one 208/120V three phase 800A feeding 6 service disconnects meter stack MLO located in sprinkler room. The second 208/120V 600A feeding service trough with 3 service disconnects located in tenant #1 space
The first electric utility service meter stack six main service disconnects two of them feed tenant #1 space, one of them feed tenant #3 space, other one feed tenant #4 space and sixth one is spare feeding nothing.
The second electric utility service 600A trough service disconnects all three feed tenant #1.
Assume each four tenant spaces are separate buildings. Note sprinkler room is in tenant space #1 enclosed by walls and can only be accessible thru outside door. Not sure if it is even considered part of tenant #1 or not.
Following are the question:
1. Would it be considered code compliant NEC 230.2 a building is only served by one utility service if meter stacks two service disconnect feeding tenant #1 are relocated to be fed from service 600A trough disconnects? That way tenant #1 electric utility would serve only tenant #1 and meter stacks utility would serve multiple tenants but their is no provision that single utility cannot serve multiple buildings. Please let me know your opinions and thoughts