Two Family Dwelling Grounding Electrode Conductors

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
I'm pretty certain this isn't a compliant method of establishing a common grounding electrode connection, but I figured that I would check.

Two family home, two panels in the basement next to each other, GEC out of one to the ground rods, GEC out of the other to the water pipe. Bare jumper installed between the grounded terminal bar in each panel.

Any thoughts?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You're correct, that's wrong. Each panel must have its own, independent electrode connections.

They may share electrodes, and shared GECs may even be tapped, but not a jumper from another panel.
 

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
You're correct, that's wrong. Each panel must have its own, independent electrode connections.

They may share electrodes, and shared GECs may even be tapped, but not a jumper from another panel.
Thanks, I was pretty sure it was a violation, but after encountering it a few times I was starting to question myself.
 