I'm looking at an application where the customer wishes to have a single transformer feed two separate LV 480V switchgear lineups located in separate buildings. The transformer is a 2000kVA transformers with a 13.8kV primary breaker and 480V secondary. The first LV Switchgear is located right next to the transformer and would likely be close coupled with bus to the transformer. Each LV switchgear lineup has (4) feeder breakers)
In trying to feed the 2nd LV switchgear lineup I see two options that would not be NEC code compliant:
Option 1: Tap the incoming bus of the 1st LVA lineup to cable feed the 2nd lineup. From what I can tell this would be a violation of 240.21 ( Tapping a tap) as well at 450.3 Note 2 requiring breakers to be grouped in a single location. Is it still considered a tap if you use cable with same ampacity?
Option 2: Run 2 separate feeders from the transformer secondary to the two LVA lineups. This however appears to violate 450.3 Note 2 as well.
In looking at this I see two options that perhaps will be NEC code compliant but wanted to get feedback from others.
Option 3: In the first lineup have a main breaker for that lineup but before that main breaker have a feeder breaker to feed over to the 2nd lineup. The 2ne lineup can then be MLO. You would have to essentially double the ampacity of the first switchgear lineup. (800A to 1600A). The other option would be to just have (5) feeder breakers in the first lineup with no main breaker (one feeding 2nd lineup) so that both lineups would not have mains. This would not be idea for coordination.
Option 4: If I put a CT on the secondary bushings of the transformer and I have those CT's connected to a relay on the 13.8kV primary breaker can I count those CT's as a secondary main protection? If so then then I can run the two separate feeders from the transformer secondary to the lineups because the feeders will be on the load side of the CT's which are serving as the secondary transformer protection and secondary conductor protection. Is there any reason why I can count these secondary CT's as the secondary protection. To me this seems like the best approach.
In trying to feed the 2nd LV switchgear lineup I see two options that would not be NEC code compliant:
Option 1: Tap the incoming bus of the 1st LVA lineup to cable feed the 2nd lineup. From what I can tell this would be a violation of 240.21 ( Tapping a tap) as well at 450.3 Note 2 requiring breakers to be grouped in a single location. Is it still considered a tap if you use cable with same ampacity?
Option 2: Run 2 separate feeders from the transformer secondary to the two LVA lineups. This however appears to violate 450.3 Note 2 as well.
In looking at this I see two options that perhaps will be NEC code compliant but wanted to get feedback from others.
Option 3: In the first lineup have a main breaker for that lineup but before that main breaker have a feeder breaker to feed over to the 2nd lineup. The 2ne lineup can then be MLO. You would have to essentially double the ampacity of the first switchgear lineup. (800A to 1600A). The other option would be to just have (5) feeder breakers in the first lineup with no main breaker (one feeding 2nd lineup) so that both lineups would not have mains. This would not be idea for coordination.
Option 4: If I put a CT on the secondary bushings of the transformer and I have those CT's connected to a relay on the 13.8kV primary breaker can I count those CT's as a secondary main protection? If so then then I can run the two separate feeders from the transformer secondary to the lineups because the feeders will be on the load side of the CT's which are serving as the secondary transformer protection and secondary conductor protection. Is there any reason why I can count these secondary CT's as the secondary protection. To me this seems like the best approach.