Is a pedestal meter main considered a structure?
A single family dwelling is fed by a meter main pedestal. The property owner wants to operate a 125 amp phase converter in his attached garage. The garage is already contains a sub panel that will not accommodate this new load.
Art.225.30 requires all separate structures to be fed by no more than one feeder.
Can I run a new feeder to the garage for the phase converter? Since I am dealing with one structure ( If the pedestal is not a structure) would this be compliant.
Thanks John