Two Fire Pump Disconnect switches?

Status
Not open for further replies.

cvirgil467

Senior Member
Location
NewYork
We have an installation where we have a service rated fusible switch in between the utility service and the fire pump controller. The service rated fusible switch is supervised via pad lock in the closed position.

The fire pump controller has a main circuit breaker and a transfer switch integral to the fire pump controller.

Per 695.4-B (2008 NEC), I am allowed a single disconnecting means.

Does the main breaker integral with the fire pump controller count as two disconnect, and therefore I need to remove either the service rated disconnect or remove the main circuit breaker at the fire pump controller?

Thanks
cvirgil
 
We have an installation where we have a service rated fusible switch in between the utility service and the fire pump controller. The service rated fusible switch is supervised via pad lock in the closed position.

The fire pump controller has a main circuit breaker and a transfer switch integral to the fire pump controller.

Per 695.4-B (2008 NEC), I am allowed a single disconnecting means.

Does the main breaker integral with the fire pump controller count as two disconnect, and therefore I need to remove either the service rated disconnect or remove the main circuit breaker at the fire pump controller?

Thanks
cvirgil

No! You can't remove anything from the listed controller and you can have both disconnects. But that fusible switch between the POCO and the FP controller will have to be rated to carry the locked rotor current indefinitely. While you did not mention the HP, that usually makes for a very large switch.
I would add that for most garden variety FP installs it would not be typical to have a disconnect between the POCO and the FP controller as all full service FP contrllers are SUSE rated.
 
No! You can't remove anything from the listed controller and you can have both disconnects. But that fusible switch between the POCO and the FP controller will have to be rated to carry the locked rotor current indefinitely. While you did not mention the HP, that usually makes for a very large switch.
I would add that for most garden variety FP installs it would not be typical to have a disconnect between the POCO and the FP controller as all full service FP contrllers are SUSE rated.

^^^^^^^
What he said.
 