We have an installation where we have a service rated fusible switch in between the utility service and the fire pump controller. The service rated fusible switch is supervised via pad lock in the closed position.
The fire pump controller has a main circuit breaker and a transfer switch integral to the fire pump controller.
Per 695.4-B (2008 NEC), I am allowed a single disconnecting means.
Does the main breaker integral with the fire pump controller count as two disconnect, and therefore I need to remove either the service rated disconnect or remove the main circuit breaker at the fire pump controller?
Thanks