I installed a 100amp service for a sign driving only one ground rod. The inspector wants a second rod I know I must drive it no closer than 6 ft. But dose the EGC be a solid run (unbroken) from gr 1 to gr2 and to meter base, or can I clamp on gr1 to gr2 with solid wire and leave gr2 with separate solid wire to meter?
 

George Stolz

Moderator
Staff member
250.64(F) says you can do either.

If you install a conductor between the meterbase and a ground rod, it is a GEC. If you install a conductor between a pair of electrodes, it is a bonding jumper. See 250.53(C) for it's requirements.

Check this out, and take note of how the conductors are shown in the diagram. Perfectly compliant with the NEC. ;)
 