I'm working with a GE/ABB Powermark panel with two neutral/ground buses. The buses do not have a bonding strap installed from the factory.
The panel came with two green screws, one preinstalled on the right bus. The left bus has a hole for the second screw which came in a bag.
I will land my GEC on the right bus, the service grounded conductor on the left bus, and bond the two buses together via #6 cable. The main service disconnect is inside this panel.
I'm hesitant to use the second screw on the left side bus.
If a load neutral conductor is landed on the right bus, load current could travel into the right screw, through the enclosure, and out the left screw to the service.
Or is this how it's supposed to be installed and I don't need the #6 bonding jumper?