I do maintenance and hvac on a campus. I was called to look at a small ice machine that was not working. There is a gfci outlet behind the machine that has been tripping. There is also a gfci at the main panel. Can it be problematic to have two gfci s in one circuit? Is there any benefit?
The manual for the machine says to not put it on a gfci outlet because it can cause nuisance trips. The outlet though is less than six feet from a sink. I recommended moving the ice machine which the person that resides there was opposed to. If there is a gfci at the breaker, can the other be replaced with a non gfci outlet?
There is also a garbage disposal in the same circuit. While the instructions dont recommend dedicated circuits for either, I thought it was common practice to isolate them. Perhaps this just depends on the equipment and situation. Any insight is appreciated. Thank you!
The manual for the machine says to not put it on a gfci outlet because it can cause nuisance trips. The outlet though is less than six feet from a sink. I recommended moving the ice machine which the person that resides there was opposed to. If there is a gfci at the breaker, can the other be replaced with a non gfci outlet?