volts said:when using two ground rods , is it require to run single ground wire for both ground rods or separate grounds for each
SiddMartin said:if you do use a jumper, gotta use irreversible crimp on the connection
SiddMartin said:if you do use a jumper, gotta use irreversible crimp on the connection
infinity said:
Jim W in Tampa said:that picture wasted an acorn,wire could have gone thru the first one to the second.Was no need to cut the wire
Jim W in Tampa said:that picture wasted an acorn,wire could have gone thru the first one to the second.Was no need to cut the wire
iwire said:Sidd lets assume we have a service with just two ground rods for the electrodes.
The conductor from the panel to the first ground rod is the GEC and can only be spliced with irreversible means.
However the conductor from the first rod to the second rod is not a GEC it is a bonding jumper and you can splice it and terminate just like any other conductor.
Check out this NEC handbook image.
![]()