physis
Senior Member
These are the same two stupid service panels on a two family dwelling. :?
Inspector today says I have two services therefore I have to have two separate ground rods, one for each service.
One question I have is:
Are two separate meter combos connected from one drop for a two family dwelling one, or two, services?
I can't tell from articles 100 and 230.
The other thing is, I don't know if anybody's heard this before, when I asked for a code reference that prevents me from using a single ground rod or both of these panels I got "I don't have to give you a code reference, you have to prove to me that you can do it", You can probably guess my response, although I was nice about it.
I tried to find something that supports his claim but I couldn't, that's why I asked for the reference.
Is there anything that says I need two rods?
Inspector today says I have two services therefore I have to have two separate ground rods, one for each service.
One question I have is:
Are two separate meter combos connected from one drop for a two family dwelling one, or two, services?
I can't tell from articles 100 and 230.
The other thing is, I don't know if anybody's heard this before, when I asked for a code reference that prevents me from using a single ground rod or both of these panels I got "I don't have to give you a code reference, you have to prove to me that you can do it", You can probably guess my response, although I was nice about it.