I have a setup where there are two motors and a couple of non motor loads on one branch circuit. The largest motor is 2 HP @ 230V = 12A by the table. The other is 1 HP @ 230V = 8A by the table. The non motor loads are 2A, or probably less, combined.
If you take 125% of the largest load, you get 12A * 1.25 = 15A
Add the 2nd motor
15A + 8A = 23A
Add the non motor loads
15A + 8A + 2A = 25A
This is all fed from a 30A 2-pole 240V GFCI breaker on #10 AWG.
The motors are then fed from the load side of a time clock and also within sight of the breaker/panel. The non motor loads are direct line power. All loads are fed by #10 AWG.
Had an inspection and the inspector is concerned about the motors not having individual OCPD. He wasn't sure and said he would look into it.
The motor section in the code is very confusing to me, but I think 430.24,Table 430.28, and 430.53(D) would allow my installation.
Is my install compliant, or do I need individual OCPD for each motor?
Also might help to know that the two motors are pool/spa pump motors and have built in overloads.
Any help on this would be appreciated!
I believe you set up requires individual protection
430.53 Several Motors or Loads on One Branch Circuit. Two or more motors or one or more motors and other loads shall be permitted to be connected to the same branch circuit under conditions specified in 430.53(D) and in 430.53(A), (B), or (C). The branch-circuit protective device shall be fuses or inverse time circuit breakers.
(A) Not Over 1 Horsepower. Several motors, each not exceeding 1 hp in rating, shall be permitted on a nominal 120-volt branch circuit protected at not over 20 amperes or a branch circuit of 600 volts, nominal, or less, protected at not over 15 amperes, if all of the following conditions are met:
- The full-load rating of each motor does not exceed 6 amperes.
- The rating of the branch-circuit short-circuit and ground-fault protective device marked on any of the controllers is not exceeded.
- Individual overload protection conforms to 430.32.
(B) If Smallest Rated Motor Protected. If the branch-circuit short-circuit and ground-fault protective device is selected not to exceed that allowed by 430.52 for the smallest rated motor, two or more motors or one or more motors and other load(s), with each motor having individual overload protection, shall be permitted to be connected to a branch circuit where it can be determined that the branch-circuit short-circuit and ground-fault protective device will not open under the most severe normal conditions of service that might be encountered.
(C) Other Group Installations. Two or more motors of any rating or one or more motors and other load(s), with each motor having individual overload protection, shall be permitted to be connected to one branch circuit where the motor controller(s) and overload device(s) are (1) installed as a listed factory assembly and the motor branch-circuit short-circuit and ground-fault protective device either is provided as part of the assembly or is specified by a marking on the assembly, or (2) the motor branch-circuit short-circuit and ground-fault protective device, the motor controller(s), and overload device(s) are field-installed as separate assemblies listed for such use and provided with manufacturers? instructions for use with each other, and (3) all of the following conditions are complied with:
- Each motor overload device is either (a) listed for group installation with a specified maximum rating of fuse, inverse time circuit breaker, or both, or (b) selected such that the ampere rating of the motor-branch short-circuit and ground-fault protective device does not exceed that permitted by 430.52 for that individual motor overload device and corresponding motor load.
- Each motor controller is either (a) listed for group installation with a specified maximum rating of fuse, circuit breaker, or both, or (b) selected such that the ampere rating of the motor-branch short-circuit and ground-fault protective device does not exceed that permitted by 430.52 for that individual controller and corresponding motor load.
- Each circuit breaker is listed and is of the inverse time type.
- The branch circuit shall be protected by fuses or inverse time circuit breakers having a rating not exceeding that specified in 430.52 for the highest rated motor connected to the branch circuit plus an amount equal to the sum of the full-load current ratings of all other motors and the ratings of other loads connected to the circuit. Where this calculation results in a rating less than the ampacity of the supply conductors, it shall be permitted to increase the maximum rating of the fuses or circuit breaker to a value not exceeding that permitted by 240.4(B).
- The branch-circuit fuses or inverse time circuit breakers are not larger than allowed by 430.40 for the overload relay protecting the smallest rated motor of the group.
- Overcurrent protection for loads other than motor loads shall be in accordance with Parts I through VII of Article 240.
Informational Note: See 110.10 for circuit impedance and other characteristics.
(D) Single Motor Taps. For group installations described above, the conductors of any tap supplying a single motor shall not be required to have an individual branch-circuit short-circuit and ground-fault protective device, provided they comply with one of the following:
70-324
- No conductor to the motor shall have an ampacity less than that of the branch-circuit conductors.
- No conductor to the motor shall have an ampacity less than one-third that of the branch-circuit conductors, with a minimum in accordance with 430.22, the conductors to the motor overload device being not more than 7.5 m (25 ft) long and being protected from physical damage by being enclosed in an approved raceway or by use of other approved means.
- Conductors from the branch-circuit short-circuit and ground-fault protective device to a listed manual motor controller additionally marked ?Suitable for Tap Conductor Protection in Group Installations,? or to a branch-circuit protective device, shall be permitted to have an ampacity not less than one-tenth the rating or setting of the branch-circuit short-circuit and ground-fault protective device. The conductors from the controller to the motor shall have an ampacity in accordance with 430.22, The conductors from the branch-circuit short-circuit and ground-fault protective device to the controller shall (1) be suitably protected from physical damage and enclosed either by an enclosed controller or by a raceway and be not more than 3 m (10 ft) long or (2) have an ampacity not less than that of the branch-circuit conductors.