eric9822
Senior Member
- Location
- Camarillo, CA
- Occupation
- Electrical and Instrumentation Tech
I have an existing installation of a 1200 HP 2300V motor. A project manager that likes to think way outside of the box would like to install a backup for this motor but avoid the expense of adding another motor starter. His proposal is to add a "switch" at the location of the motors that would allow the existing starter to feed either motor one at at a time. Section 430.87 specifies that each motor shall have its own controller with a few exceptions, none of which says you have a transfer switch downstream of the controller, I would like to kill this idea quickly. My gut instinct says that by the time I spec out an adequate transfer switch and add the proper interlocking to prevent switching while the motor is running and prevent running both motors from running I will exceed the cost of a starter. The whole thing sounds ridiculous anyway. Is 430.87 enough to kill the idea?