Two neutrals SEC

Status
Not open for further replies.

Rayne

Member
Location
Oklahoma
Occupation
Learning
It looks like there are two neutral wires coming off the neutral messenger wire going Into the weather head, if anyone has any explanation for this I would appreciate it, just studying for home inspection purposes thanks.
85F09629-62EE-4291-B269-43B82D173C75.png
 
There are 2 meters feeding two different apts or parts of the building. A neutral is needed for each apt. Not sure -- maybe I misunderstand
 
There are 2 hots connected to one ungrounded conductor, 2 hots connected to the other ungrounded conductor and 2 neutrals connected to the grounded conductor
 
Looks like they didn't have a large enough conductor so they tried to parallel two smaller ones. Not compliant at all since I doubt those wires are 1/0 or larger
 
It means instead of using a number 2 conductor (not sure what size they needed) they used 2- #6 or so to make the conductor larger
 
Basically you are doubling the size of the conductor by doing that. Inside the meter those 2- conductors are installed under the neutral lug.
 
It means instead of using a number 2 conductor (not sure what size they needed) they used 2- #6 or so to make the conductor larger
What would be a reason someone would do that and what would it look like in the meter , would both of those wires be wrapped together to become one wire under one lug then ?
 
What would be a reason someone would do that and what would it look like in the meter , would both of those wires be wrapped together to become one wire under one lug then ?

Yes, If the installer didn't have the larger conductor then he could use 2 smaller conductor that equalled the size of the larger one he didn't have, however, I doubt what he did was legal.
 
Yes, If the installer didn't have the larger conductor then he could use 2 smaller conductor that equalled the size of the larger one he didn't have, however, I doubt what he did was legal.
Okay that makes sense thanks , any chance it could be #1 on this picture where the grounding conductor comes from the service drop, I’m sure there no way anyone would know by a picture
003F9C0D-28EB-4EC2-B1E0-35B2211793B3.png
 
You'll have to pull the meter and see how it's terminated to know for sure. As dumb as it sounds it could be a GEC passing through the meter enclosure.
 
You'll have to pull the meter and see how it's terminated to know for sure. As dumb as it sounds it could be a GEC passing through the meter enclosure.
That’s exactly what I was wondering , so that’s kinda what it seems like it’s narrowed down too it’s either parallel neutrals or maybe a gec
 