Two or more SDS

Status
Not open for further replies.

benaround

Senior Member
Location
Arizona
If you have 2 or more SDS in the same room or area, could you loop a GEC

to all of the SDS's and then hit the building steel etc. just once ?
 
You could have a common GEC from building steel and have taps off of it to each SDS 250.30(A) 4
 