Two outdoor units….need wire and breaker size expertise

Status
Not open for further replies.

Diypbo

New User
Location
Washington
Occupation
Plumber
Here’s the situation…..Running wires for two outdoor mitsubishi mini split pumps.

#1 is 3 zones. MCA is 31.5a MOCP says 40a

#2 is 2 zones. MCA is 26.9a MOCP says 40a also

The wires will run roughly 20 ft and 24 feet from panel to disconnect boxes. And for reference, we have a preexisting 3/4 grey conduit through the wall outside already and have determined that we can fish two 10/2 wires through.

Question: is 10/2 suitable for both or just the smaller one? Any consideration to be given to two wires heat in one conduit……does the larger unit need 8 gauge?

I am simply running the wires to the boxes. Hvac professionals will be hooking up the line sets, etc. saving $1000 by running wires myself, thanks for the help!
 
You are best off leaving the electrical to the professionals. Or try DIYchatroom.com
Forum rules prevent us from assisting you
 