Thanks for the support Jim. But I should advise you (and the membership) that I have some reservations about my stated opinion.
Read the first sentence of 408.35 carefully. Note in particular the words, ?. . . of a . . . panelboard. . . .? The 42 circuit limit is for a single box. The words do not explicitly speak of 42 circuits as being the limit for a single panelboard. Does anyone interpret this sentence as saying you can have two boxes side by side, each with 42 overcurrent devices, and call this thing a ?84 circuit panelboard? (singular)? That is not my interpretation, but it is an interpretation that might be reasonably supported.