Hello All,
I have some Heat trace that is tied two pole 30 amp GFI breaker 208Volts. one leg goes through a contactor that is controlled by a temperature sensor. when the sensor opens the contactor the GFI trips within 30 seconds. there are 6 other circuits with the exact same setup that do not trip. I have put the system into "Hand" Control and the GFI does not trip unless the test button is pressed. I have left it in "hand" for 5 months with no trips. I have checked all connections and haven't found anything that would cause this that I could see. I have been scratching my head on this one and I am sure the issue is right in front of me but I cant seem to see it on this one.:?
I have some Heat trace that is tied two pole 30 amp GFI breaker 208Volts. one leg goes through a contactor that is controlled by a temperature sensor. when the sensor opens the contactor the GFI trips within 30 seconds. there are 6 other circuits with the exact same setup that do not trip. I have put the system into "Hand" Control and the GFI does not trip unless the test button is pressed. I have left it in "hand" for 5 months with no trips. I have checked all connections and haven't found anything that would cause this that I could see. I have been scratching my head on this one and I am sure the issue is right in front of me but I cant seem to see it on this one.:?