whofrankw
Member
- Location
- milford nj
Engineered speced out three phase airhandler equipment for a big gym im working on and during the estimate the equipment changed to single phase. im trying to figure out how much more amps the new equipment is going to put on the main panel. The specs so far are a 400 amp main 3 phase 4 wire 120/208v. The original equipment on the plans are 5 air handler units, 3 phase , 45 amp circuit breaker with a load of 4.2kva on each phase. The specs i have on the new 5 air handlers require two, two pole breakers. a 25amp and a 50amp which draw 17 amps and 35 amps. I want to know how much more if any are the new specs for the air hanlders going to draw. I could put this off on the engineer but i want to bring this up to the contractor first and talk it over with them too.
one more question. the original plans without the new air hanlders show a total demand of 343.91 amps on a 400 amp breaker. this is a gym and i was wondering if that load should be considered continuous and no more than 320amps
one more question. the original plans without the new air hanlders show a total demand of 343.91 amps on a 400 amp breaker. this is a gym and i was wondering if that load should be considered continuous and no more than 320amps